Just done an EICR for a thatched property, number of issues but 2 which are not so easy to fix:

1) Twin and earth cable run all around loft space, quite haphazardly (no thermal insulation around) - in a few places mice have had a little nibble at the cable. Can see underlying black/red insulation but no copper, so not major at this time.
Options: rewire in rodent proof cable
Enclose cable in conduit/trunking
Protect cable with metal capping

I'll probably be using a combination of all 3 - any other ideas?

2) Twin and earth clipped around the house for outside lights. Since being installed house has been re-thatched and now part of the cable is enclosed/covered by the thatch. Not sure how easy its going to be to get the cable out from under the thatch.
Anyone else dealt with a similar problem?
 
Observation was based on a quote from an NICEIC document regarding Electrical Installations in Thatched Buildings:

"cables and wiring systems should NOT be installed immediately under, through or over the thatch"

I appreciate that its probably been like that for a while but if i see it I'm obliged to record it.

probably a wise precaution , however youre not inspecting as per an nic dictat are you ?

or to put it another way , how are you going to record this in a report ?
as an observation ? a non compliance ?
 
or to put it another way , how are you going to record this in a report ?
as an observation ? a non compliance ?

I've put it down as a C2 at the moment. I know there is nothing specific in the regs and there can't be because of the wide range of situations with respect to external influences. But what about 422, precautions where particular risks of fire exists? Also doesn't the thatch act as an insulator?

I'm open to other perspectives into my category of observation.
 
I've put it down as a C2 at the moment.

well thats a really big call isnt it ?
not disagreeing , but......
the installation as a whole will now fail its inspection due to that C2 even though theres no damage or problems
and the repairs arent going to be that cheap either are they ?
the point im making is theres a whole load of implications arising from that single C2
so you need to be right on the money with your facts before putting pen to paper.
 
If you've got to rely on a reference to back up an assertion, rather than knowing straight away whether or not something is a REAL danger, then that's a C3.

Here's the Rockingit rationale:

C1 - It's going to kill someone sooner or later
C2 - It could kill someone sooner or later because......
C3 - It's not that great because the regs say......
OBV - It's not that great because.....
REC - It could be done better by doing.....
 
On thatched roof buildings the electrical installation within the roof space really needs to be top notch as far as safety goes, and probably why Tony stated the use of MICC!! Not sure about nowadays but i'm pretty sure the insurance companies require certain standards to be maintained before insuring/reinsuring such heightened fire risk properties....
 
There are a number of other issues that have a higher priority for remedials.

The issue with the T&E in the loft is of primary concern. Usually if there is no fauna damage I make a comment as to what wiring is fitted and mention no visible damage seen, but in this case there is some damage.
 
On thatched roof buildings the electrical installation within the roof space really needs to be top notch as far as safety goes, and probably why Tony stated the use of MICC!! Not sure about nowadays but i'm pretty sure the insurance companies require certain standards to be maintained before insuring/reinsuring such heightened fire risk properties....

Don't know of any other standards that the insurance companies can quote other than BS7671 and rely on competance.

In some cases I've seen more damage under floorboards than in loft spaces, but no one ever mentions that.

As it stands seen many new thatched properties wired totally in T&E, not an issue unless there is an ingress of fauna.
 
Electrical installations should be suitable for the environment they are installed in. Somehow i don't think typical T&E wiring cuts the mustard to my mind. Thatched roof properties have, or used to be deemed to have a heightened fire risk by insurance companies. In the old days many of these properties had metal containment in the roof spaces. No idea what happens nowadays....
 
El Thatched roof properties have, or used to be deemed to have a heightened fire risk by insurance companies. In the old days many of these properties had metal containment in the roof spaces. No idea what happens nowadays....

OK, so thatch has a heightened fire risk. Generally an electrical installation that is properly installed does not pose a fire risk, the fire risk actually happens when the electrical installation is potentially damaged, by fauna etc.

If you can guarantee to keep the fauna out then T&E could be suitable, but how do you guarentee keeping the critters out!

The Dorset Model is supposed to give guidance on wiring in Thatch but it only says:

Advice should be sought from an approved electrical contractor regarding the most

appropriate type of wiring system. Effects from rodent damage and straw debris need to

be considered and the National Inspection Council for Electrical Installation Contracting

have issued guidance to their members.


It is NOT recommended to install recessed lighting into the ceilings below the thatch. Light

fittings within the roof space to be in a bulkhead fitting. External floodlights should not be located under the eaves of the thatch.


I have a copy of the NICEIC document and its a bit woolly, doesn't say you must do this or do that. Just says x or y has proved beneficial etc. or you may want to consider z.
 
I have a copy of the NICEIC document and its a bit woolly, doesn't say you must do this or do that. Just says x or y has proved beneficial etc. or you may want to consider z.

What else did you expect from the likes of the NICEIC??

Far too many non electrical organisations/Bodies give this outfit far too much credence than they actually deserve.
 
Last one i put a heat alarm in the thatch space and the lighting points wired in SWA (feeds to switches and luckily only centre lights), MICC would of been nice but ÂŁÂŁÂŁÂŁÂŁÂŁ. Took the SWA from the switch to a conduit box that just pokes through the ceiling flush to allow easy changing of light fittings (and not remodelling the ceiling around the box)
 

Reply to Wiring in thatch loft in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
397
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
986
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
504
  • Question
My bafflement increases. I swapped the offending light with one elsewhere on the back of the house - one of those that's on a circuit of its own...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top