Wiring supply in top of Isolators RCDS and mcbs | on ElectriciansForums
Discuss Wiring supply in top of Isolators RCDS and mcbs in the UK Electrical Forum area at ElectriciansForums.net
When it goes against the manufacturers instructions???
Is this a theoretical question, or have you come across it on a job?
Isolators, it probably doesn’t matter as it’s just a switch… but mcbs and RCDs it will
if you get it the wrong way round the fuses remain live when the isolator is switched off.
One reason I like the Schneider "Quadbreak" style of fused-switch is they isolate both sides of the fuse, so you can feed either way and don't have to worry if the load is UPS-y and leaks a lot even with the supply disconnected (i.e. potentially both sides are "live").
MCBs probably not an issue.
Some RCDs can have trouble if powered from the load-side as stuff like test button is not disconnected when they fire and so can burn out. However, many RCD are OK from either end but it can be hard to get a definitive statement on that.
As above, according to manufacturers instructions. Where I am domestic and commercial CU's / distribution boards are almost always wired with supply on top and final circuits on the botton of circuit breakers / RCD's.
When I spoke to hager tech about this they said that mcbs must be fitted the correct away round as I remember it ,it was to do with the direction the arc traveled in the event of a fault or overload
I’ve been told the exact opposite from Hager technical support, direction doesn’t matter and doesn’t effect operation at all.
When fitted to a DB/CU yes, but that is to do with the mechanical arrangement and possible results of arc gasses on the cables, etc. Not electrics as such. Also some MCB do not have identical clamps on either side, so there is a further mechanical reason for which end is on the busbar.
Some MCB rated for DC use do have a direction/polarity, but for AC I can't see any reason.
As far as up/down is concerned typically on a type A board the main switch or incomer RCD is fed from the top, but then the MCB/RCBO is fed from the bottom. However, for type B boards of course it is left/right!
I asked Hager once for the RCCB in a DIN board and was told either way is fine, as I checked the data sheet, etc, and at no point did it suggest a direction, but I wanted to be sure.
The MI tell you which end to connect to the busbar, and which end goes to the outgoing circuit.
Do they? The MI for a DB will tell you which way round they should be installed in that DB, but the MI for the actual circuit breaker is unlikely to say anything about it.
If you fit a circuit breaker incomer to the DB then you will have the live side at the bottom of the incoming circuit breaker and the live side at the top of the outgoing circuit breakers.
This is what I got on 22/6/2020
Good Morning [pc1966],
Apologies for the delay, in regards to your question, the answer is no.
Our Main switches & RCD are neither pole dependant and makes no difference if you feed the supply from the top nor bottom.
I hope this answers your question.
Kindest regards,
Fraser
Technical Support
Hager Ltd
Hortonwood 50
TELFORD,Shropshire TF1 7FT
Reply to Wiring supply in top of Isolators RCDS and mcbs in the UK Electrical Forum area at ElectriciansForums.net
View: https://www.youtube.com/watch?v=glsg2HpWyok
I'm not arguing, I want to understand why some arrive at different conclusions to myself and some amount of disagreement is inherent; there's no...