worth reporting? | Page 2 | on ElectriciansForums
Discuss worth reporting? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
For me it would be a C3 as the CPC doesn't run the full length of the cable therefore not feeding the point. A warning label placed on the CU stating that only Class 2 items be used on the circuit due to lack of CPC. Departure noted on the report. Pub time...
Reply to worth reporting? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
    • Friendly
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Indeed, that was my thought, a B20 having a 60A instantanious trip should easily cover a inrush for a domestic fridge, and if the fridge and...