Would you energise a modified circuit without RCD protection | on ElectriciansForums
Discuss Would you energise a modified circuit without RCD protection in the UK Electrical Forum area at ElectriciansForums.net
O
Octopus
Pretty much what the title is.
Asked to do a job, don't have time to do the board change but could make the changes to the kitchen socket circuit...
So testing of sockets would be done, but no RCD protection (very old board so no upgrade path) until CU is changed in Jan
Tin hat on!
Pop corn at the ready.
Tin hat on!
What's wrong with the existing CU?
Modified in what way?
If installing sockets then you would be required to protect them via 30mA rcd or depending how the cables are installed they may require it also.
Even if it was temporary modified until the board change then compliance with bs7671 is still required for the works you’ve carried out when putting the modified circuit into service.
[ElectriciansForums.net] Would you energise a modified circuit without RCD protection
In all seriousness, I would consider fitting an upfront 30mA RCD to satisfy the needs of ADS unless all supplementary bonding is in place?
It's been safe enough for the last few years and if you're satisfied there's no immediate risk then potentially you could leave as is. However without knowing the state of the installation then its only your decision.
Just faffing on with tails etc adds time and journeys to the job . I would just go for the complete planned solution from the outset.
As above though - you know the state of the installation.
The job is complete when the certificate is complete ...
The owner has lived in the house for 25 years and doesn't understand why she needs a new fuseboard anyway ..................
Turn off the installation until the new CU is fitted.
yes strima ,she could go have dinner at sally armys for xmas cant she !
Reply to Would you energise a modified circuit without RCD protection in the UK Electrical Forum area at ElectriciansForums.net
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
davesparks
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...