timhoward

-
Broke Internet
Esteemed
Arms
Supporter
Joined
Jul 19, 2019
Messages
4,618
Solutions
1
Reaction score
9,847
Location
Oswestry
I had Scottish Power moving a supply this morning from one building to another so an extension could be built. I had everything ready for them with a Wylex REC2 in the meter box and I'd already run my tails.

Anyway, they turned up, , ran their ducting, stuck the head in, connected up to my isolator, did their tests, said "all good, Ze 0.22" and disappeared.

I finished connecting up the other end, did all the dead tests etc. then it came time to energise.
So I turn on the isolator. Nothing. Suspected 2 pole tester first and dug out the proving unit, but no it was fine. Tested top of isolator, live, tested bottom of isolator, nothing. Checked other switch position in case I'd been a muppet, no, still nothing.
As I was in the middle of nowhere in glorious remote Wales this was quite a problem. I explained the issue to the customer and they offered to go to Toolstation for me to get another one (45 minutes round trip) while I finished off. Happy days.

In the meantime I finished a few other things, and still waiting for the customer I started to look through the bag of rubbish from the DNO which had some interesting unused items e.g. CNE pole connection kit, and then I saw there was a brand new unused Proteus service isolator in their rubbish...!

So I possibly set a new record for summoning the fuse fairy to a cut-out that was less than an hour old, swapped the isolator, and all good. The customer was happy to come back and find the power on, and he can of course return the one he got.

I don't think I've ever known a Wylex product not work out of the box. First time for everything.
 
I had Scottish Power moving a supply this morning from one building to another so an extension could be built. I had everything ready for them with a Wylex REC2 in the meter box and I'd already run my tails.

Anyway, they turned up, , ran their ducting, stuck the head in, connected up to my isolator, did their tests, said "all good, Ze 0.22" and disappeared.

I finished connecting up the other end, did all the dead tests etc. then it came time to energise.
So I turn on the isolator. Nothing. Suspected 2 pole tester first and dug out the proving unit, but no it was fine. Tested top of isolator, live, tested bottom of isolator, nothing. Checked other switch position in case I'd been a muppet, no, still nothing.
As I was in the middle of nowhere in glorious remote Wales this was quite a problem. I explained the issue to the customer and they offered to go to Toolstation for me to get another one (45 minutes round trip) while I finished off. Happy days.

In the meantime I finished a few other things, and still waiting for the customer I started to look through the bag of rubbish from the DNO which had some interesting unused items e.g. CNE pole connection kit, and then I saw there was a brand new unused Proteus service isolator in their rubbish...!

So I possibly set a new record for summoning the fuse fairy to a cut-out that was less than an hour old, swapped the isolator, and all good. The customer was happy to come back and find the power on, and he can of course return the one he got.

I don't think I've ever known a Wylex product not work out of the box. First time for everything.
A good recovery from yourself. Have fitted many Wylex isolators and have never had an issue. Guess you were just unfortunate on this occasion.
 

Reply to Wylex REC2 service isolator failure in the Electrical Tools and Products area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

Similar threads

Thanks, I was reasonably confident but nice to confirm. That was the original install getting power to the outbuilding, done by an electrician we...
Replies
8
Views
431
You could try this https://www.deskshare.com/ip-camera-viewer.aspx Ive got one similar to this but i think only ever used it a few times...
Replies
5
Views
869

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top