Yet another induction hob question | on ElectriciansForums

Discuss Yet another induction hob question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Joined
Jun 25, 2019
Messages
2
Reaction score
0
Location
Norwich
Hello

I have a new AEG induction hob rated at 7.4kw max using power sharing but AEG do not specify a cable size or mcb rating nor will they answer the question I submitted to them by email. I think their position is that it is down to the electrician to decide.

The configuration is as follows:

Cooking zone 1 - 2300/3700/10
Cooking zone 2 - 1800/2800/10
Cooking zone 3 - 1400/2500/4
Cooking zone 4 - 1800/2800/10

Where the values represent Nominal power (max)/Power function/Power max duration (mins)

As the work is notifiable I have asked a local qualified electrician to quote for a new radial circuit and he has suggested that I need 10mm cable on a 40 amp mcb because he does not apply diversity and therefore the amperage will be 32.174 at 230 volts, hence the need to go to a 40 amp mcb and 10mm cable. He is prepared to install 6mm cable on a 32 amp mcb but will not be responsible for the frequent tripping out that he feels I may experience.

Having read a number of different forums I get the impression that most electricians (but not all) would apply diversity and I would appreciate the views of those of you experienced in this area as to whether I am likely to regret not going with the 10mm cable and 40 amp mcb. My personal feeling is that it won't be a problem as I am unlikely to ever be using all four zones on the 'power' function at the same time. Using all four zones on maximum (but without 'power') would require 7.3kw, so just within the limits of a 32 amp mcb but this isn't going to happen either.

The only reason for posting the question is that ideally I would like to use the existing cooker switch for the induction hob (it's right next to it) and run a new radial to the double oven which is currently on the existing cooker circuit. The existing circuit is 6mm cable on a 32 amp mcb.

The existing cable is 9.5 metres from the CU to the cooker switch and passes through the ceiling void and is then enclosed in conduit behind a tiled wall. It does not pass through any insulation.

I would very much appreciate your thoughts based on personal experience.

Thanks in advance.
 
Just get a different electrician who knows what he's doing..
corrected that for you.

6mm on a 32A MCB is fine. ref. method permitting you could use 6mm on a 40A. (Iz =47A ref. method C ).
 
If the electrician uses 240v, which is more likely, then a 32 mcb will be ok as max would be less than 31 amps. Ask the "electrician" to check whether it is 230 or 240v.
 
The electrician is wrong in my opinion.

Diversity on cooking appliances in domestic locations is first 10A and 30% of remainder. Has been for years and years. Following that rule has never let me down. The existing circuit will easily cope with the load.

I fairly often install single ovens and hobs such as yours on a single 32A supply. Hob is usually around 7kW and oven around 2.7kW
 
Many thanks to all for taking the time to reply. There are other local electricians and I will get another quote which will hopefully be in line with the opinions expressed here.

Thanks again.
 

Reply to Yet another induction hob question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
453
  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
701

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top