As I said in my first post, there were other loads, not just the data centre. I’ve worked on this system and it’s not a simple one to understand. Two villages, a medical centre, several pubs, farms and a number of separate companies supplied from it. The system wasn’t designed, it evolved over about 60 years.
 
In the area I work often two transformers are run in parallel at the same time and it is the nornal running arrangement. As Tony mentioned the tap changers are run in a master slave arrangement. The protection side is a work of art and I have been trying for some time to get involved. Directional protection, restricted earth fault etc very interesting and specialised stuff
 
As I said in my first post, there were other loads, not just the data centre. I’ve worked on this system and it’s not a simple one to understand. Two villages, a medical centre, several pubs, farms and a number of separate companies supplied from it. The system wasn’t designed, it evolved over about 60 years.


Fair enough Tony, i know only too well, sometimes explaining or describing things that are not exactly as one would expect, ...can be a real pain in the bot!! Especially when they have evolved over that period of time...
 
In the area I work often two transformers are run in parallel at the same time and it is the nornal running arrangement. As Tony mentioned the tap changers are run in a master slave arrangement. The protection side is a work of art and I have been trying for some time to get involved. Directional protection, restricted earth fault etc very interesting and specialised stuff

I know it's not unheard of to run 2 11KV TXs in parallel, but i can assure you it's not your normal standard practice to do so. The main Switchboard along with it's ACBs/GCBs/SW Fuses etc, would need to be rated at the combined fault level (bracing etc) of those 2 TX's, ...That tends to make such switchboards a rather expensive proposition.

It's also one of the reasons why a ring of RMUs fed from 2 TXs on the same switchboard are normally run in an open ring configuration.

As you say, it's the art of setting up protection relays and controls that is the real specialised area, be it for HV/MV/LV switchboards, and systems.
 
I’ve paralleled 11/.44KV 1600KVA transformers several times and each time we knew we would be exceeding the boards maximum fault level but for only a mater of seconds. The chances of a fault on the board in that space of time would be minimal.
This was a modern system but due to the failure of a VCB it was decided all VCB’s were to be taken out of service in turn and tested. We did all we could to make the operation as safe and quick as possible, it wasn’t possible to shut the plant down. One beauty of this particular system was every boards loading was such that if one transformer failed the other could take the full load. When I first saw the system I thought it laughable that a transformer capable of supplying 2133A was bumbling along at say 900A only when we had to go through this exercise did I realise how good it was. OK some bits of kit had to be shut down where there was no parallel feed, (11KV motors) for a few minutes while we swapped the VCB for a stand by one.
The four incoming 33/11KV 20MVA transformer OLTC’s were always in leader and follower mode.

At another works two of us were separately asked to write a switching procedure so part of the intake board could be shut down, we compared them and made the final out of the two. There were 77 steps to the procedure, a lot of load shedding, a lot of driving and radio contact, but most things kept going!
 
I’ve paralleled 11/.44KV 1600KVA transformers several times and each time we knew we would be exceeding the boards maximum fault level but for only a mater of seconds. The chances of a fault on the board in that space of time would be minimal.
This was a modern system but due to the failure of a VCB it was decided all VCB’s were to be taken out of service in turn and tested. We did all we could to make the operation as safe and quick as possible, it wasn’t possible to shut the plant down. One beauty of this particular system was every boards loading was such that if one transformer failed the other could take the full load. When I first saw the system I thought it laughable that a transformer capable of supplying 2133A was bumbling along at say 900A only when we had to go through this exercise did I realise how good it was. OK some bits of kit had to be shut down where there was no parallel feed, (11KV motors) for a few minutes while we swapped the VCB for a stand by one.
The four incoming 33/11KV 20MVA transformer OLTC’s were always in leader and follower mode.

At another works two of us were separately asked to write a switching procedure so part of the intake board could be shut down, we compared them and made the final out of the two. There were 77 steps to the procedure, a lot of load shedding, a lot of driving and radio contact, but most things kept going!

Never worked on such large networks, and TX's the biggest network i had to deal with was on the Libyan Great Man Made River Project. Which was a sub-distribution from 66 Kv feeds down to the well fields some 600+ km into the Sahara desert, feeding 2 sub-station/distribution centres (66KV/33KV/11KV) that went on to feed numerous TXs around the well fields for pumping purposes and supplying purpose built self contained maintenance villages. Everything in the sub-stations on the 66KV side was SF6 Gas filled (by ABB), looked more like a pumping station, than a anything to do with electrical...lol The 33KV and 11KV side of things was via conventional M/Switchboards (by MG), But all breakers were GCBs.

Can't remember the size of the main 66KV TXs at the 2 well field substations, but they were big buggers, and never really had any dealings with them to be honest, except the repair of one tail leg that failed on the secondary side that went to earth via a nice clean hole thru the tail insulation about 12mm in dia and a dammed black, burned, and deformed cable protection cover, about a metre from the failed tail!! ...lol!!

Most of the TXs i was involved in were 33KV and 11KV, mostly the later ranging from 1 to 3MVA, but with pretty sophisticated relay/auto control and protection all the same.

By the way, all the main switchboards WERE rated for the full fault current of the respective connected TXs in paralleled configuration, and tested as such, but normal operation was with open bus couplers, 3 to a switchboard.

I won't tell you what the Libyan supplying main distribution centre in Benghazi was like, except it scared the crap out of me, walking round the place!!! lol!!! :vanish:
 

Reply to You’ll love this. in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
596
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
774
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top