E
eskimo39
I did some sub contracting today for a local company who had a lot of testing to do at a factory. I was helping an oldish chap who was using an old Metrel Easytest.
When doing a Ze test he set the unit to Z Line and took the reading (0.11 ohms) however I asked him to do it on Z loop and got a reading of 48.4 ohms.
He didn't know what the Z Loop function did and had always used the Z line for testing. Can anyone shed some light on this feature.
Coinsidently I went and got my Fluke 1652B from the van and did the same test on the mains using the Loop Z (No Trip) feature and the setting for L-PE which gave the result as 48.7ohms, I then pressed the F1 button and changed the setting to L-N which gave 0.11 ohms.
Does anyone know of a guide on which settings to use for each test on the Fluke 1652b? I did my T&I with a megger I owned and the fluke is new to me. Also when would you have to choose between 'No Trip' and 'Hi Current' on the meter
Are these tests, functions correct>
Ze - Loop ZI (No Trip)
Zs - ????????
R1 + R2 - Continuity R LO
Insulation Resistance - Insulation R ISO
RCD - T RCD Time on AUTO
Cheers and sorry for the ignorance
Zs - ????????