Here's a question regarding Zdb.

when changing a consumer unit in a property that has sub mains, do you just test up to the sub main and ignore it from there on? I can only assume so, well that's what I do, you can't be responsible for the circuits off the submains.
 
Here's a question regarding Zdb.

when changing a consumer unit in a property that has sub mains, do you just test up to the sub main and ignore it from there on? I can only assume so, well that's what I do, you can't be responsible for the circuits off the submains.

Can't you ? A separate SOTR is in order here appended to the rest of the paperwork.
 
Here's a question regarding Zdb.

when changing a consumer unit in a property that has sub mains, do you just test up to the sub main and ignore it from there on? I can only assume so, well that's what I do, you can't be responsible for the circuits off the submains.

No you test the submain, how would you go about testing up to the submain anyway??
Final circuits fed via that submain you wouldn't necessarily expect to be tested.
 
Zdb is Zs so it is acceptable to measure or calculate. That's what the BYB says isn't it?

Any bonding is at the MET or EMT, not any other boards.

Tin hat on obviously!

Main bonding should be connects back to the MET or EMT but it could go via a subDB.
 
We remove the bonding cables to get an accurate Ze and because we cannot presume the resistance value of the bonding will be a stable figure, however when we measure Zs we leave the bonding in place so we are using part of that 'instabilty' in our 'measured' value of Zs??
.

No, that's not the reason.
We measure Ze without the main bonds connected to ensure that the reading we get is the earthing system and not the extraneous parts, thus we ensure that we are actually testing the ,means of earthing.
Measuring With the bonds connected could actually be testing via the neighbours means of earthing via a common metallic service and fail to identify a broken/high resistance suppliers earth.
 
No you test the submain, how would you go about testing up to the submain anyway??
Final circuits fed via that submain you wouldn't necessarily expect to be tested.

Thats what I usually do, test to the next layer / db at the end of the sub main. It depends, if it's off the board I would but if on Henley blocks I wouldn't.
 

Reply to the thread, titled "Zdb Question" which is posted in Periodic Inspection Reporting & Certification on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top