Hello All,

New assembly line going in at factory I work at. All single phase assembly stations with lights and sockets or screens and tooling etc.

All our existing lines are supplied via local distribution boards but this new line is having a Zucchini 3 phase overhead busbar installed.

When we installed and tested our current stations, I took a Zdb reading at the distribution board but the busbar system has got me thinking.......would I still need to take a Zdb reading (of sorts) at the busbar tap off box?

If so, this poses me another problem, once the cover is removed, all power is lost from the tap off box (as you would expect) so I am not entirely sure how I would take the reading? Only way I can think of is to keep a tap off box purely for testing with a socket connected to it on a short length of cable which I could them use for taking the Zdb.

Thanks for any advice.

ATB

Chris
 
Thanks for your reply Rob, that makes complete sense.

I will have to ask the lads installing the busbar for the Zdb reading, it is being connected to an ancient MiniForm board which our landlord refuses to let us anywhere!

No problem with the Zs at the other end.

Thanks again for your help.

ATB

Chris
 
The only way I can think of taking a Zs reading at the busbar connection point is using the socket on a short cable is mentioned in my original post.

The fuse connections etc within the tap off box are isolated as soon as the cover is opened. I can of course, take Zs at the end of the assembly station circuit and I do this at present when connecting to the distribution boards.

ATB

Chris
 

Reply to Zdb testing on busbars in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
2
Replies
24
Views
3K
I have a few 30 amp and 63 amp ottermill overhead Busbar tap off boxes for sale after a factory relocation, these are becoming hard to locate now...
Replies
0
Views
491

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top