ze 1.9ohms | Page 2 | on ElectriciansForums

Discuss ze 1.9ohms in the Australia area at ElectriciansForums.net

Joined
Jan 30, 2009
Messages
42
Reaction score
1
just been to quote for a added socket. nice new 17th edition board, so thought all should be ok. quick check of efli gives me a zs of 2.2ish ohms.same on a few more sockets. so goes to main board and checks ze,which is 1.9 ohms. a tad to high for tn-s at 0.85. now if this was a tt system that would fine. as its a tn-s would you contact the dno to rectify it? or would you leave alone and add the socket as its rcd protected? i will ring the dno and see if i get anywhere with them which i doubt.just wandered what anyone else would do.now be honest:wink5:
 
Why would they be looping in/out, when being fed from an overhead supply?? I think your getting confused with a ground supply system, that's the only time i've seen service cut outs looping to the next property, and even that was a long time ago.
 
i have seen a few installations that have had service cut outs looped on an overhead supply. mainly terraced houses with an overhead supply feeding one house then clipped along house to next house
 
More fool to the DNO's then, what a waste of cable!! i see that were talking about very rural situations here, where maybe these rows of terrace houses were fed from the end of an overhead string. ....If not, i can't see what the advantage was, wiring these houses that way... lol!!
 

Reply to ze 1.9ohms in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

Similar threads

Thanks I re tested this morning as I had other bits to finish off . I tested three times and it was 0.30 every time . It may have been my leads...
Replies
7
Views
2K
  • Question
I think I might be tempted to test this theory, if it can be done without causing danger to anyone.
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top