Are you refering to the 80Ka on bs88's or did i miss something ?
Clue
MCBs 6Ka rating PFC reading 19.1Ka
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Ze and distance from substation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Are you refering to the 80Ka on bs88's or did i miss something ?
Customer is not rushing to sort this out, but wants to speak with me next week about it. Assuming for the moment that the measured value of Ze=0.01 ohms is correct, I am trying to establish what can potentially be done about this. To recap: TN-S, the DB circuit breakers are 6kA SCC, the DNO fuse is BS1361 type II 100A 33kA SCC, PFC is 19.9kA
So the DNO fuse will withstand the PFC, but the MCBs will not. Can we rely on the DNO's fuse to protect the installation? What about the potential for harm to the MCBs (and persons, livestock and property) at that level of fault current?
I would read the warning that all MCB manufacturers give regarding the PFC and MCBs