Noob2013

Hi all,

Im about to start the 2nd year of my apprenticeship and have been practising my testing at my parents home. I have a query on some results.

The Ze reading was 0.00 ohms and the PFC was 10kA. It's a PME Supply.

The Ze seems too low, does that mean that is is a very good reading or something is not right?

Also, does is the PFC reading ok?

Thanks in advance.
 
did you discount the main earyhing conder from met as you do not wanna any parrl earth paths for the ze as its the total extral earth path
 
Yeah Main Earthing Conductor was disconnected.

Would the reading not get higher if the main earthing conductor was connected?
 
Last edited by a moderator:
@ 10KA, the Ze will be around 0.02 ohms. your meter will probably see this as 0,00. to get round it, either don't null the leads and take off their res. after, or use a few metrews of cable then deduct that.
 
If the fuse type is unknown, its better to assume the breaking capacity is 16.5kA. The fuse could be a Bs 1361-1 or a Bs 88-6. But in the OPs case, the 10kA is still lower than the 16.5kA.
 

Reply to Ze and PFC reading? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
514
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top