Not if the main fuse is a 1361 rated at 60 or 100a as the upstream breaking capacity of these is 33ka.

What is the regulation regarding this, I would think that if the Ka is higher than the protective device this is a defect.

I tested an install once that had old MCBs (needed changing anyway but that's another story)

The Ka on that board was >7 Ka I can't remember exact figure, the three phase 3871s where rated at a maximum of 3 Ka.

The overload for this distribution board was BS88 so obviously they would withstand the Ka.

My argument would be that the three phase MCB is not rated to that Ka and so may cause unknown issues under max fault conditions.

People's comments please and if I'm wrong on this (better safe than sorry) please be gentle
 
I've seen and fitted mcb's type B that were 10KA rated. Hager, Eaton etc. RCBO's tend to be less I've noticed. I've also measured Ze as 0 when close to tranny but I've always known that below 0.2 standard meters aren't that accurate. An engineer once discussed pfc with me saying that sometimes you need to create some impedance on the incoming legs do this to drop it to a level the switch gear could handle.
 

Reply to Ze and PFC reading? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top