Electricalserv

0.01ohms? Does this comply? Tns system. Unsure because, usually given as 0.8ohms, previous test cert gives 0.08 ohms. Not sure if previous spark rang supplier or just put 0.08 anyway. Is this value ok anyhow?
 
Last edited by a moderator:
Its quite possible to have a pfc that high especially if the transformer is nearby.

It is theoretically possible to approach values above 16KA but in practice, it's almost unheard of.

Since becoming aware of the scenario that I described in post 11, any conventional Ze measurement that we find below 0.10 Ohms is re-measured with an adjusting impedance added to lift the meter into it's acceptable range (normally above 0.30 Ohms).

The difference always makes this a worthwhile 10 minute exercise and shows how poor our meters are at values below 0.30 Ohms.
 
Well if you have a 1000kva transformer, using a transformer impedance of 4.75% you would get 30.5ka at the terminals, so if your close to the transformer a high PFC is possible.

Absolutely right but from my point of view as a serial measurer of Ze, I have yet to actually measure a value of Ze low enough to give a PFC higher than 16kA
 
Well here you have it. Nulled leads etc. Remeasured 0.02 ohms 11.5ka 20m from substation. This is the house my bro has just bought. Previous test result was 0.08 ohms so very low aswell.....
 
Last edited by a moderator:
It is theoretically possible to approach values above 16KA but in practice, it's almost unheard of.

Since becoming aware of the scenario that I described in post 11, any conventional Ze measurement that we find below 0.10 Ohms is re-measured with an adjusting impedance added to lift the meter into it's acceptable range (normally above 0.30 Ohms).

The difference always makes this a worthwhile 10 minute exercise and shows how poor our meters are at values below 0.30 Ohms.

i regularly find high pfc readings iq, had one recently.01 ze off the scale ipf. what would be your course of action in that situation?
 
i regularly find high pfc readings iq, had one recently.01 ze off the scale ipf. what would be your course of action in that situation?

No, your meter displayed a reading of 0.01 Ohms, read back through the thread, the bit regarding 2nd digit tolerance, it makes a massive difference to PFC as you can imagine when a Ze reading can be between 0.01 and 0.09 Ohms.

The only way to increase accuracy at those levels is to use a known resistance in series to lift the meter into it's 'sweet spot' accuracy area.

I wrote a piece on how and why to add the resistance, I'll find it following my house move and get it posted up.

If you do a lot of testing, it's well worth doing this 10 minute procedure.

Out of interest, check your meter's quoted accuracy range-a Megger 1553 is >0.30 Ohms!
 
You can always calculate the Ze at origin, like we used to have to do, before Loop Testers were around!! Get an accurate volt meter and a load of around 40 to 50A. Measure the voltage at no-load, and then with the connected load, there will be a voltage drop. Whatever the voltage drop difference measured, divide by the current you applied, ...that's your value!!! You can then go onto find the PSC by dividing the no-load voltage, by the figure you attained above....

At the very least it will give a good indication if your meters measured value, is anywhere near accurate. Your only problem being, ...is providing a known current load to measure the volt drop. We used to have home made load banks, that we made as part of our training. But any steady load can be used of sufficient current to cause a volt drop at the origin of your supply.
 
Last edited by a moderator:

Reply to Ze at origin tns in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
855

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top