You can always calculate the Ze at origin, like we used to have to do, before Loop Testers were around!! Get an accurate volt meter and a load of around 40 to 50A. Measure the voltage at no-load, and then with the connected load, there will be a voltage drop. Whatever the voltage drop difference measured, divide by the current you applied, ...that's your value!!! You can then go onto find the PSC by dividing the no-load voltage, by the figure you attained above....
At the very least it will give a good indication if your meters measured value, is anywhere near accurate. Your only problem being, ...is providing a known current load to measure the volt drop. We used to have home made load banks, that we made as part of our training. But any steady load can be used of sufficient current to cause a volt drop at the origin of your supply.