How do you find the the Ze of a diesel generator when power a building, for example a 400kw unit?

In so far I have FLC of 1,110 amps. 7.5 (L-E) x 1,110 = 8327. 120/8327= 0.015 ohms

Somehow this seems just to easy.
 
The machine's own resistance and reactance would normally dominate for a bolted fault at the main panel. The stator reaction depends on the magnitude and phase of the current w.r.t the EMF, not the terminal voltage. The difference between the two is no longer nominal nor hidden behind the AVR.
 
It will, but whether it makes a significant difference is less clear.

Your example 400 kcmill supply cable is a little bigger than our 185mm (for which I have a table handy) where the cable Z is about 20% higher than R due to inductance, where as the 4/0 AWG cables are a little bigger than our 95mm size where the difference is around 5%.

With large cables, transformers, etc, it is always best to run the calculations using the full information of X & R values and then see what comes out, even if in reality something like a 5% difference is likely lost in the uncertainty of fault magnitude, etc.


Alright and agree.

However, what R & X to I assume for the generator windings when doing the equation to get the total Zs? And what voltage? I know this is a dynamic 4-D scenario, but I want to keep it simple (if practicable) to a 2-D set of equations.
 
The machine's own resistance and reactance would normally dominate for a bolted fault at the main panel. The stator reaction depends on the magnitude and phase of the current w.r.t the EMF, not the terminal voltage. The difference between the two is no longer nominal nor hidden behind the AVR.


As I am reading up on it, and I could be wrong, the kw on the prime mover actually drops due to the R going down and the X going up. The current is reactive, and as the voltage goes down the field is "forced" to its max excitation to keep voltage up.
 
As I am reading up on it, and I could be wrong, the kw on the prime mover actually drops due to the R going down and the X going up. The current is reactive, and as the voltage goes down the field is "forced" to its max excitation to keep voltage up.


Anyone know? R goes up as shirt circuits move away from the generator.
 

Reply to Ze of Generator in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
947
  • Question
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
    • Like
    • Winner
Replies
0
Views
676

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top