N

nicsin02

Hi guys, i am testing a 3-phase D/B tomorrow and its supply is only a 4-core cable so its earth comes from the Gland-frying pand and then a flying lead to the earth bar, normally doing domestic property i would disconnect earth for Ze ensuring no parralell paths, what would be the norm on this occasion? thanks guys
 
same procedure but measure o each of the phases. reconnect earthing conductor for PFC reading. ensure installation is isolated before dissing earth. if it's a sub-board, the EFLI is noted as Zdb
 
just remove any bonding cables.... and clip on to rail.... f its a PIR put it down as a limitation...!

if you take gland off and damage it putting it back on or damage teh strands it will be hell to fix..!
 
in that case, i would disconnect any bonding conductors and the fly lead. i might get shot down , but i would prefer that to the possible risk of compromising the integrity of the glanding by disconnecting . apart from the risk of having 3 live phases flopping about unglanded.

- - - Updated - - -

beaten to it by torpedo fingers. GRRRR>
 
must be getting old. bloody heart attack slowed me down. making a good recovery now i'm back on a few beers, though.
 
If this is a swa feed would this mean it is a sub-board or a feed from a switched fuse as in both cases its not a Ze but a Zdb (Zs).
Its not normal to have a swa feed in the usual sense of a supply without it going through another device.
 
yeah its a sub mains fed from another board, i know its a Zdb but would still have to fill it in the Ze section for the new sub board or am i wrong lol?
 

Reply to Ze on a SWA in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
319
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
844
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
967

Similar threads

Sounds more positive.
Replies
8
Views
619
  • Question
All the lamp post cutouts I've ever seen have a twin swa gland plate built in to the base.
Replies
2
Views
640
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top