Ze on a SWA | Page 2 | on ElectriciansForums
Discuss Ze on a SWA in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
yeah its a sub mains fed from another board, i know its a Zdb but would still have to fill it in the Ze section for the new sub board or am i wrong lol?
Actually, you're wrong.:smile:
It's Zs of the sub-main and you don't disconnect anything to measure it.
The only place you measure Ze is at the origin of the installation - and for this you disconnect the 'Earthing Conductor'.
What you are talking about disconnecting is the CPC of the SWA (Sub-main)..........and for a Zs measurement this is left connected.
If, on the other hand, your 3 phase board had it's own 'earthing system' (e.g. a seperate earth rod), then you could treat it as a seperate installation, with it's own origin and 'earthing conductor'..........then you could measure Ze at your board.
Completely agree, you will be measuring nothing but the Zs at a sub-distribution board.
At the main incoming position of that sub-board, your value can be stated as Zdb, and can be noted no doubt in the Ze position of your certificate for this sub-board, with a an explanation in the remarks column. The rest of the sub-boards circuits, will again be tested as normal for Zs values.....
Reply to Ze on a SWA in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Sounds more positive.
All the lamp post cutouts I've ever seen have a twin swa gland plate built in to the base.
loz2754
L