yeah its a sub mains fed from another board, i know its a Zdb but would still have to fill it in the Ze section for the new sub board or am i wrong lol?

Actually, you're wrong.:smile:

It's Zs of the sub-main and you don't disconnect anything to measure it.

The only place you measure Ze is at the origin of the installation - and for this you disconnect the 'Earthing Conductor'.

What you are talking about disconnecting is the CPC of the SWA (Sub-main)..........and for a Zs measurement this is left connected.

If, on the other hand, your 3 phase board had it's own 'earthing system' (e.g. a seperate earth rod), then you could treat it as a seperate installation, with it's own origin and 'earthing conductor'..........then you could measure Ze at your board.
 
Actually, you're wrong.:smile:

It's Zs of the sub-main and you don't disconnect anything to measure it.

The only place you measure Ze is at the origin of the installation - and for this you disconnect the 'Earthing Conductor'.

What you are talking about disconnecting is the CPC of the SWA (Sub-main)..........and for a Zs measurement this is left connected.

If, on the other hand, your 3 phase board had it's own 'earthing system' (e.g. a seperate earth rod), then you could treat it as a seperate installation, with it's own origin and 'earthing conductor'..........then you could measure Ze at your board.

Completely agree, you will be measuring nothing but the Zs at a sub-distribution board.

At the main incoming position of that sub-board, your value can be stated as Zdb, and can be noted no doubt in the Ze position of your certificate for this sub-board, with a an explanation in the remarks column. The rest of the sub-boards circuits, will again be tested as normal for Zs values.....
 

Reply to Ze on a SWA in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
842
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
965

Similar threads

Sounds more positive.
Replies
8
Views
619
  • Question
All the lamp post cutouts I've ever seen have a twin swa gland plate built in to the base.
Replies
2
Views
640
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top