Ze on campsite

Hi all.
Currently working on a campsite installing new hook up points. Just had a new 3 phase supply installed. Each phase feeds a separate consumer unit which in turn feeds 4double hook up points each. The supply is tncs up to the hook ups (protecting the swa) and tt at the hook ups. The ze at the hook ups varies from 240 ohms to 790 on one earth rod. Anyone got any good ideas on lowering the ze, as at the moment the rcd's aren't operating due to the high earth path I'm assuming!
Thanks
Tom
 
not sure if that reply posted then. What i mean is that the pme from the supply is used to protect the armoured cables, but it does not enter the hook up points as pme is not allowed to supply the caravans. Sorry if i didnt explain very well. Is this not the standard way of going about this then?
Thanks for all the fast replies
 
so the tncs cannot be used to protect the armoured then?! its easy to disconnect them from the supply and swap it to the tt at the hook ups, i thought that it could be used however though as its not supplying anything portable.
 
can anyone clarify whether its ok to keep the pme protecting the rcd's or if i need to swap it over to the tt side?
would it be acceptable to link all the armoureds on each particular run inside the single phase board, then all the hook ups could benefit from each others earth rod, as well as sticking one by the single phase.
 
sorry, they are actually rcbo's on the hook ups. one for each outlet. There is a 100mA rcd protecting the individual armoureds from the supply.
I would have a quick flick through the regs book but its not one of the books i keep on my bedside table. Thinking maybe i should now!
 
Thats fine its the PEN conductor of the hook up point that needs to be connected to an earth electrode , reg 708.553.1.14 the RCD's are required to disconnect both live and neutral reg 708.553.1.13 , as for the armoureds if its terminated into a metal clad board with the proper glands then the armour will be connected together assuming the cable runs go back to the same CDU
 
sorry, they are actually rcbo's on the hook ups. one for each outlet. There is a 100mA rcd protecting the individual armoureds from the supply.
I would have a quick flick through the regs book but its not one of the books i keep on my bedside table. Thinking maybe i should now!
may be a good idea its section 708 page 190
 