Morning All,
Just a quick one thats got me stumped. Got my NIC assessment coming up so wanted to run this one past you! Im doing a barn conversion, basically dist circuit from customers house to CU then obviously onto final circuits. Now ive taken all the supply characteristics from inside the house, where the cut out fuse is. Now when ive done all the Zs tests, ive just used measurement, including for lighting circuits. What im wondering is if the assessor whats me to CALCULATE the loop impedance, how do I go about it, do I need to take into account the dist results? Bit of additional info, its a TT system, ive installed seperate earth rods at all dist boards (dist circuit supplies garage, barn conversion, then play house).
One more quicky, just wanted to confirm zs results, being a TT system theyre obviously higher than the tabulated results, would I be right in saying that as long as theyre under 200ohm thats acceptable? Results are actually around the 12ohm mark, which if im right in comparing to the 200ohm limit is pretty reasonable?
Cheers again folks!
Just a quick one thats got me stumped. Got my NIC assessment coming up so wanted to run this one past you! Im doing a barn conversion, basically dist circuit from customers house to CU then obviously onto final circuits. Now ive taken all the supply characteristics from inside the house, where the cut out fuse is. Now when ive done all the Zs tests, ive just used measurement, including for lighting circuits. What im wondering is if the assessor whats me to CALCULATE the loop impedance, how do I go about it, do I need to take into account the dist results? Bit of additional info, its a TT system, ive installed seperate earth rods at all dist boards (dist circuit supplies garage, barn conversion, then play house).
One more quicky, just wanted to confirm zs results, being a TT system theyre obviously higher than the tabulated results, would I be right in saying that as long as theyre under 200ohm thats acceptable? Results are actually around the 12ohm mark, which if im right in comparing to the 200ohm limit is pretty reasonable?
Cheers again folks!