Sorry, I've read all this but I still don't understand why your disconnecting the earth at each DB to carry out the test. What cable type of cable is supply them? And are you turning the DBs off before you carry the test out? Also are you reconnecting the earths before you move on to the next test?
Requirement for the Power station is that every distribution board must have a Ze reading captured - Zs readings captured on outgoing circuits.
Ze - The value of Ze is measured at the intake position on the supply side with the earthing conductor disconnected.
The main isolator / MCB is always turned off before disconnecting the supply earth, thus no outgoing circuits are energised from the DB.
Yes lol, if the earths weren't being reconnected after testing, I'm pretty sure we would all be down the road!