Hi all have a problem with zs readings on final circuit of 4.4

so tested ze which was also in the same region 4.00

tested r1 + r2 which were ok (dead test) 0.25

tested ze again now a reading of 0.37

tested socket again 0.68

tested again ten min later 2.7

went next door as the two houses are feed from this house
They were the same when reading good on one house same the other and when bad so was next door.

i think a bad supply earth but can't understand why the fluctuations. When nothing moved etc

the supply is a tns as stated above feeding two houses.

any ideas
 
I assume that the supply is actually looped from the first house to the second rather than both going through one meter.
With a TNS earth it could well be that the cable is damaged somewhere out in the road.
It could also be that the batteries are flat on your meter or you are doing a trip lock test.
However as baker says could be the earth connection at the service head that is poor, that is the first thing to check, is the earth coming form the cable sheath properly sweated in place or is it a BS951 clamp. Is the connection of this cable to the MET secure and uncorroded, are the connections from the MET to CU secure (less likely considering the supply to next house)?

If you have checked these and the Ze is still not stable then call the DNO and ensure they are aware that the Ze is unstable, they may then check again.
 
I assume that the supply is actually looped from the first house to the second rather than both going through one meter.
With a TNS earth it could well be that the cable is damaged somewhere out in the road.
It could also be that the batteries are flat on your meter or you are doing a trip lock test.
However as baker says could be the earth connection at the service head that is poor, that is the first thing to check, is the earth coming form the cable sheath properly sweated in place or is it a BS951 clamp. Is the connection of this cable to the MET secure and uncorroded, are the connections from the MET to CU secure (less likely considering the supply to next house)?

If you have checked these and the Ze is still not stable then call the DNO and ensure they are aware that the Ze is unstable, they may then check again.

Yes sorry it is looped from one to another

did both trip lock an no trip lock just to see
batteries new

cal ok
tester checked on my house on known zs ok every time so I assume tester ok


Extra info service cable comes into house 1 and splits to at service head
the earth coming from the cable sheath also splits to each property looks to have a clamp on it (covered in self amalgam tape) don't want to disturb it for now

from the cable sheath it goes to a met then to cu same next door.


i will contact DNO tell them it is unstable see what happens
will let you know.
 
DNO came out today and told customer readings were ok
i phoned them and arranged to met them on site

reading was terrible said it was not like that earlier yeh no kidding told them that .

now replacing head and connection to cacable oh and the customer told me it was pass the blame phoned Scottish power who said no Scottish gas who than said no it councils because of house next door .

agreed to fix but said it could be tomorrow or 4 to 5 weeks

glad house is rcd protected at least that gives some protection house next door is older fuses so very bad told them to complain.

Thanks again for the replaysreplays
 
DNO came out today and told customer readings were ok
i phoned them and arranged to met them on site

reading was terrible said it was not like that earlier yeh no kidding told them that .

now replacing head and connection to cacable oh and the customer told me it was pass the blame phoned Scottish power who said no Scottish gas who than said no it councils because of house next door .

agreed to fix but said it could be tomorrow or 4 to 5 weeks

glad house is rcd protected at least that gives some protection house next door is older fuses so very bad told them to complain.

Thanks again for the replaysreplays


hay like the tv there not replays reply is what I typed. Stupid auto correct
 

Reply to Ze readings change in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
401
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
989
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!
2
Replies
22
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top