Just carried out a ze on a tt istallation and got a reading of 156 m ohms, carried the same test out a few months before and got 132 m ohms, the zs results were slightly higher as well! Could this be due to the changing conditions of the weather as to we're the earth rod is placed.

Thanks chris
 
Just carried out a ze on a tt istallation and got a reading of 156 m ohms, carried the same test out a few months before and got 132 m ohms, the zs results were slightly higher as well! Could this be due to the changing conditions of the weather as to we're the earth rod is placed. Thanks chris

What earth rod(s) did you use, ...a single 3/8'' non extendable rod, or a single 5/8'' extendable rod?? And how far from the house external wall did you locate your rod??



Yes. Think temperature and the amount of moisture in the soil. TT in the Sahara wouldn't be too good

Not exactly correct, i have installed 9 TT systems on a multi location project in Libya, one being 900Km from the coast into the Sahara desert. The worst value obtained was from memory being 0.87 ohm or thereabouts. But then we were using proper 3/4'' 3.2 metre copper clad rods. Just needed to use enhancement mortar, in this case Bentonite!! The Sand in the Sahara is literary full of sulphates and chlorides, so quite conductive in it's own right. Furthest 2 installation didn't get any annual rainfall, so irrigation systems was also installed to maintain earth field moisture content...


Also susceptible areas of corrosion to the large pipe line, were protected with passive cathodic protection using magnesium strings, also with Bentonite mortar. Results were very positive to say the least!! Not all sands are the same!! lol!!
 
Last edited by a moderator:
If it was a new rod installation I'd expect the impedance to improve steadily over the fist year as the soil around the rod settles. Also I'd expect a better result in winter due to higher soil moisture content. If your impedance has increased over the last few months I'd earmark the rod for regular monitoring to try to establish it's stability. If you're in doubt it hopefully isn't too much of a job to add a 2.3 meter extension to it and whack it in deeper.
 
... TT in the sahara wouldn't be too good

Sahara sand is actually quite conductive due to the dissolved minerals and salts it contains. Granite areas in Cornwall are a real challenge. Certain limestone areas in Dorset are tricky also, the last installation we did for MOD required a copper mat the size of a football pitch to meet the required specification, because the soil depth was so shallow.
 
Sahara sand is actually quite conductive due to the dissolved minerals and salts it contains. Granite areas in Cornwall are a real challenge. Certain limestone areas in Dorset are tricky also, the last installation we did for MOD required a copper mat the size of a football pitch to meet the required specification, because the soil depth was so shallow.

And very expensive too!!

Limestone areas depend on whether the limestone is fractured limestone or not. If it's of the fractured type then bore holes/Bentonite would have been a far better solution, and costs greatly reduced too!! lol!!
 
Hi,

Just to throw a bit more into the mix. I have used Bentonite on a number of occasions as E54's post where the soil resitivity has been very low; and always used Austentitic rods ( Stainless coated rods 12mm dia ) in the presence of Cathodic Protection. One to chew over.

Regards
 

Reply to Ze result different from a few months ago. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Thanks for the reply littlespark. Yes the works have been carried out. Surely it is fraudulent because basically the document is Not...
Replies
2
Views
549
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
831
Thanks Dave, I appreciate the reply as I knew it was something I wasn’t picking up.I’ll read up in the regs book on an IT supply as Can’t say I’ve...
Replies
4
Views
1K
The only way to find out is ring the DNO and ask them and will. Tell you straight away. What system is in place.
Replies
14
Views
2K
  • Question
Just a small correction..
    • Like
    • Informative
    • Agree
Replies
6
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks