N
nickblake
Evening chaps a periodic today walked through the front door and my concerns were were raised just glancing at the supply cable and cut out and yes my concerns were right ,and obviousley the electrical contractor never tested the supply infact the installation as this would have thrown up the fault or error , i have come across this so many times now its worrying , when you carry out a Ze test you should isolate the supply disconnect the main bond to the board then carry out your test , this install the main earth had been connected to the cutout earth block although it was obviouse it was not a TNCS but a TNS supply the wire had been cut off the TNS earth (again) and connected to the earth block which was not connected in the cutout (this was confirmed by testing the neutral to the earth block and it was open circuit) the whole house was not earthed with the bonds and all earths connected the Ze reading was 696 ohms , so redoing the test connecting to the TNS connection the reading was 0.60 ohms , then making the connection properly this dropped to 0.29 ohms . so a little message when testing or connecting your Earth bonds to the cut out earth blocks check to see if its connected first