I just had the DNO come out as I was getting a reading of 2.68ohms on a TNS system measured from the CU.
All parallel paths removed.

The DNO measured 0.68 at the supply and changed the earth strap and got it down to 0.48.

Is there any reasons why this is so high at the CU ?

There is an earth bar near the meter which has lost its shine - could this be the problem ?
 
If you are measuring direct from the supply tail at the CU then I would suspect a loose connection on the line terminal as it comes in.
If you are measuring through the switch then it may be some resistance in the switch.

Have you tried measuring from the earth bar at the CU, then at the MET and then at the supply earth directly, this should indicate where the change occurs, it may be just a loose dirty connection on the MET if you were measuring from the earth bar a the CU.
Take out all the connections (not the line incomer! just tighten it) clean the copper if necessary and re terminate this should clear the problem.
 
Did the DNO try it with their meter where you measured it high?
Just wondering if it's as simple as a problem with your meter, or even measuring using no-trip setting on a 1700 MFT.
 

Reply to Ze too high on TNS at CU but not on supply in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
316
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
962

Similar threads

Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!
2
Replies
22
Views
1K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top