Hi I'm new here, I'm a second year apprentice.

When we do domestic testing such as a eicr my boss says that he can 'work out' R1 + R2 by taking the ZE from the ZS however i don't think this is correct as everyone would just do it?? I just wanted to confirm that this isn't correct as i do need to learn the correct way to test new installations for the future and for my college exams.

THANKS
 
Unfortunately your boss is wrong. You should not calculate the R1 + R2 from the Zs although it is deemed acceptable to calculate Zs from a measured R1 + R2.
 
Zs usually has parallel paths to earth, often through gas and water pipework, which would lower the Zs and reduce the calculated R1R2. So it would be incorrect to calculate R1R2 in that instance. I was taught that R1R2 should always be measured.
 
It is definately not the correct way due to parallel paths as already said. In fact, the cpc could be completely open circuit and totally relying on parallel path for continuity. Your boss is not alone though, there are many that calc like this though as it gives them a figure for the box and makes out they carried out the dead test. He would be better to just LIM the R1 & R2 box and just record Zs on a EICR. That is perfectly acceptable if agreed with client and very common on commercial EICR's. He should really be doing it all on a domestic though due to easy isolation and small amount of circuits tbh.
 
Last edited:
agreewith above posts. R1+R2 should be measured before energising circuit/s. then Zs measured when circuit/s is/are live.
 
Hi I'm new here, I'm a second year apprentice.

When we do domestic testing such as a eicr my boss says that he can 'work out' R1 + R2 by taking the ZE from the ZS however i don't think this is correct as everyone would just do it?? I just wanted to confirm that this isn't correct as i do need to learn the correct way to test new installations for the future and for my college exams.

THANKS

As a second year apprentice (or anyone working in this industry), you need to get your notation correct. In this case we know what you meant, but an examiner may not be so lenient.

You've used Ze, ZE, ZS, zs, r1, r2, R1, R2, some of which have meanings other than the ones you needed.
 
Zdb + (R1+R2) will give you your actual Zs.
That's the way it should be calculated.
In my opinion low current loop testers are completely inaccurate so I would prefer to see it done this way.
Definitely never the other way around!
 
Agree with the above Ze/Zdb + (r1+r2) you cannot go wrong with measuring a cable resistance with its connections.You can do a loop test get a aceptable result however with other paths fails to show the cpc that has come out /loose of a terminal.I is the electrical installation that should be tested.A paralell path could go tomorrow with the removal of a copper water pipe.
Also agree with the comment on loop meters we sent 4 off t be calabrated/checked within spec got them back plugged them into a known socket and got a range of readings but all within tolarance.
 
One thing I also find is that you can get higher earth loop readings when doing a non trip test due to the R.C.D. So doing the dead test gives you a better idea of what your actual resistance is.
 

Reply to Ze - zs = r1 + r2? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
221
The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
945

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top