Hi I'm new here, I'm a second year apprentice.
When we do domestic testing such as a eicr my boss says that he can 'work out' R1 + R2 by taking the ZE from the ZS however i don't think this is correct as everyone would just do it?? I just wanted to confirm that this isn't correct as i do need to learn the correct way to test new installations for the future and for my college exams.
THANKS
I have a 1720 myself. I know there are sparks who do calc Zs (Zs-Ze=R1&R2), but it can potentially be very inaccurate when you take into account parallel earth paths. The megger is basically doing this for you and it encourages the bad practice.Sorry to drag this up again and I always measure R1+R2 but why do some testers like the MFT1730 have the facility to measure R1+R2 using Ze as a reference. Or have I had a bit of a mental block?
I have a 1720 myself. I know there are sparks who do calc Zs (Zs-Ze=R1&R2), but it can potentially be very inaccurate when you take into account parallel earth paths. The megger is basically doing this for you and it encourages the bad practice.
They do it cause some people want it and it is an extra feature that other testers don't have.
No not really, if you had a gun you dont have to shoot someone with it. At the end of the day, as a qualified electrician, you can put whatever you deem fit in the R1 + R2 box, it is only a model form taken from non statutory regulation.So at the end of the day even though its bad practice its still acceptable to the powers that be?
Thanks for your replies, I'm in a protracted discussion about this subject and the people involved are using the fact that the meter
has the facility makes it acceptable practice. I disagree for all the reasons given in this thread.
I measured a Ze on a TT the other day and it was 197Ω, Zs on the ring was 73Ω so by using Ze - Zs = R1 + R2 I get an R1 + R2 of -124Ω that's a damn fine conductor!
I can't see how it could ever be acceptable to calculate R1+R2 this way.
well spotted, hawkeye.Is the title in this thread wrong? Shouldn't this (unacceptable) practice be Zs - Ze = R1 + R2
well spotted, hawkeye.
I have a 1720 myself. I know there are sparks who do calc Zs (Zs-Ze=R1&R2), but it can potentially be very inaccurate when you take into account parallel earth paths. The megger is basically doing this for you and it encourages the bad practice.