it's not exacly mobile homes as in caravans. it's those prefab homes like a large static. but set on bricks. called park homes. and the swa armour is providing the earth
 
it's not exacly mobile homes as in caravans. it's those prefab homes like a large static. but set on bricks. called park homes. and the swa armour is providing the earth

OK, we'll go with this for now.

The thing I would be more concerned about, rather than the Zs of the 'prefab home' installation(as this is RCD protected), would be this:

How are the services entering the 'home' (extraneous), bonded to the MET.
Bearing in mind that the MET, technically, is at the cut-out.

Unless I'm mistaken, where PME conditions apply, the Main Bonding Conductor has to be sellected in relation to the supply neutral conductor (up-stream of the cutout), and I don't think the armour of 6mm 2-core will suffice - I might be wrong.
It certainly isn't good enough with a resistance of 49.28 ohms.:)
 
yuo're right there. i assume that originally it was tns, from MET is 16mm to jubilee clip on SWA, then approx 80m to home where earth taken off SWA. Manweb, or whoever it was called then, converted this mess to PME some years ago. at the moment all i am concerned about is making it safe. will discuss options for improvement once i,ve done the best i can with what's there
 
Last edited:
It certainly sounds like the jubilee clips might be your main problem - you've got high resistance joints somewhere.......is it not possible for you to gland both ends into an appropriate enclosure.

The 16mm should be alright at the cutout end - you could use same size at 'home' end.

Just need someone to confirm the 'copper equivalent CSA' of 6mm 2-core SWA.


then approx 80m to home where earth taken off SWA.

Does 6mm work out okay for 'volt-drop' over 80 meters?
 
Last edited by a moderator:
there is a guide that gives swa csa,s.i dont think 6mm will comply.if you tt the supply at meter position you will comply as long as swa csa is 6mm
 
DSCF0168.JPGgone back today, traced back to here. took pic after removing 2 bare 2.5 earths from jubilee clips. fine mess. love the socket directly wired to tails! ripped it all out. TT'd it. got to return to relace twin socket with RCD socket. got rained off
 
and we get accused of ripping people off to put things right when the kettle has been working fine for years!
 
nick, seen the pic? that is not a problem? nother prob. the 16mm incomer is from the pole cut-out. assumed that the 2 6mm were load side. i terminated the 16mm into an isolator and re-inserted the fuse so as to restore power to the 4 homes i had dissed. wallop! one of the 6mm is now live. caught it with my elbow, OUCH. seems there are 2 feeds into this bag of trticks. made safe when rained off.
 
Last edited:

Reply to Ze & Zs-- unacceptable readings in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
731
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
972

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top