Apologies mods if this doesn't quite fit in this section I think it may.
Problem..
1)
A lot of my maintenance work takes place in a very busy Veterinary hospital, to shut down the hospital to get Ze would be impossible,if I needed to run a new circuit, I believe the regs. state it is an acceptable solution to gain Ze "By enquiry" and add this to my R1+R2 to obtain Zs do you think this is a satisfactory way of working ?
2)
When I did the 2392 recently I was specifically told by the NICEIC that is now NOT acceptable to measure Zs on circuits other than those that you can put a plug top into ie rings/sockets, as the Zs on these types of circuits can be obtained by calculation of Ze+R1+R2, and so conforms more to Electricity at work regs. that states where possible Live work must only be undertaken IF necessary.
I would be interested to hear your views on this and your working practises
ATB Steve
Problem..
1)
A lot of my maintenance work takes place in a very busy Veterinary hospital, to shut down the hospital to get Ze would be impossible,if I needed to run a new circuit, I believe the regs. state it is an acceptable solution to gain Ze "By enquiry" and add this to my R1+R2 to obtain Zs do you think this is a satisfactory way of working ?
2)
When I did the 2392 recently I was specifically told by the NICEIC that is now NOT acceptable to measure Zs on circuits other than those that you can put a plug top into ie rings/sockets, as the Zs on these types of circuits can be obtained by calculation of Ze+R1+R2, and so conforms more to Electricity at work regs. that states where possible Live work must only be undertaken IF necessary.