hi all, I posted about this recently and didn't manage to get back online till now.
I've got a Fluke 1653b multi function meter. In the last few weeks it has stopped recording Ze and Zdb readings ( readings on L-E setting) are 0.00 and on L-N reading are0.00 and PFC is 10kA ( this only happens on tncs and tns systems)
I've noticed that the Zs readings can vary quite a lot if taken at a socket outlet etc. Within seconds of testing it.
It was last calibrated in June. Do you think it's a fault with the tester or are the leads on their way out. Changed batteries.
Anyone experienced this before, I need my tester pretty much daily, how can I sort this out asap.