The 21 ohms is the DNO earth at their supply transformer. No matter what system of earthing you have in your house the supply transformer will have an earth electrode and that is the DNO responsibilty

If you have TNS or a TNC_S then the DNO have the responsibility to maintain that earth.

If you have a TT then it's the consumers responsibilty to maintain that not the DNO so they don't have the responsibilty of your Ze at a TT. All they have to ensure is that the Electrode at the transformer is there at that 21 ohms. and it is your responsibilty to get the earth path back to it.
 
The 21 ohms is the DNO earth at their supply transformer. No matter what system of earthing you have in your house the supply transformer will have an earth electrode and that is the DNO responsibilty

If you have TNS or a TNC_S then the DNO have the responsibility to maintain that earth.

If you have a TT then it's the consumers responsibilty to maintain that not the DNO so they don't have the responsibilty of your Ze at a TT. All they have to ensure is that the Electrode at the transformer is there at that 21 ohms. and it is your responsibilty to get the earth path back to it.

I would agree that it is the consumers responsibility to maintain a low resistance electrode 200ohms or less at the installation, however if the DNO did not maintain a source electrode of 20 or 21 ohms max then the earth fault path would be incomplete for TT, I know that in addition the source electrode is there for referencing the neutral of the transformer for the TN systems and voltage purposes, but this does not preclude it from a TT system, by enquiry to the DNO their standard quote for TT will be that the source electrode is 20 or 21 ohms which is an external impedance ie Ze which in turn is a requirement of the ESQCR
 
The Ze in a TT changes with the weather and is unreliable so we don't really know it; isn't that why its RCD'd

To overcome this we should install and earth electrode 2.4m deep opposing a 1.2m deep electrode. as this will be more stable than the 1.2m deep one even with a higher resistance.
 

Reply to Ze in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
683
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
969

Similar threads

you must be very close to the transformer.
Replies
1
Views
274
I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
347

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top