Shoeman

Three years ago my house had a Ze of 0.37ohms, this year on periodic done last week the Ze reading was 42.7ohms, this is more like a TT system.
What could be the cause.
External supplier at fault ?
Any help gratefully accepted.
Thanks
Shoeman
 
Three years ago my house had a Ze of 0.37ohms, this year on periodic done last week the Ze reading was 42.7ohms, this is more like a TT system.
What could be the cause.
External supplier at fault ?
Any help gratefully accepted.
Thanks
Shoeman

What did the electrician that carried your PIR have to say about this high Ze value??
I ask, because as far as i know, it would have been his duty to inform the DNO responsible for your supply. This can be/is a dangerous situation not only for you, but your neighbours too. A reading of this level indicates a joint in the supply cable, or the cable itself is breaking down, depending on what earthing arrangement has been supplied to you by the DNO.
 
as i see it we don't know which reading is correct, the system mat be TT and the first test was done without removing main bonding next door may have had a PME conversion and the bonding was giving a low reading,

It could be a TNS and the sheath has gone,

It could be a PME with a poor joint,

as E54 says what did the tester say about it?
 
Without knowing what the earthing arrangement is we are fumbling in the dark guys. Best wait for the OP coming back on that before we think about remedies. As he states this is like a TT system I do think he may have a problem though
 
as a pure guess given the info, i would say tt originally tested without being disconnected and picking up parallel paths OR a problem on the dno side a quick call should confirm the earthing arrangement
 
i did it the other day ring power for earthing arrangment and they said the electrician should no, was an electrician and i said do you not need to provide me with this info, she replied il take you details and get somone to get back to you.. following day
 
Assuming the Ze has been measured correctly (properly calibrated meter) then it should be reported to the DNO as a matter of urgency and preferably a temporary RCD fitted for additional protection. I would suggest that contacting another electrician may be a good idea as the that should have been the action taken by the electrician that measured the Ze at that latter level.
 
next door have had lots of building work done over the past couple of years including having their property rewired. could be an Issue. My electrician says that 3 years ago his full test showed my installation to be TNS. Will contact supply authority ASAP
 
Without wishing to set you off into a panic this is way above the permissible level for a TNS system. In your position I would ring the DNO as it is their earth arrangement that has the problem and it is their legal duty to maintain it. If you have any reason to doubt it you could also get another spark in to verify that the original Ze test was carried out correctly.Whereabouts are you based, I'm sure we would have a member near you who wouldn't charge a great deal for this
 

Reply to Ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
828
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
924

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top