When measuring Zs values, does everyone apply the correction factors for temperature during fault conditions to the value?
 
the max. figure is, IMO, that given in BS7671., not some guesstimate of 0.8x because of a non-specified guessed temperature the cable might be at.
 
no u times the regs values by 0.8 and the ones in the OSG have already been corrected
0.8 and 80% are the same thing surely? I meant i would measure zs of a circuit, take the maximum value and if its below the osg value then great there's room for manouver but of course the maximum values are in the bgb so as long as its below that its fine
 
0.8 and 80% are the same thing surely? I meant i would measure zs of a circuit, take the maximum value and if its below the osg value then great there's room for manouver but of course the maximum values are in the bgb so as long as its below that its fine

my thoughts exactly
 
0.8 and 80% are the same thing surely? I meant i would measure zs of a circuit, take the maximum value and if its below the osg value then great there's room for manouver but of course the maximum values are in the bgb so as long as its below that its fine

Those figures are for the Designer. The Inspector should ensure that the measured value does not exceed the corrected value.
 
If the circuit has already been energised, and has been at full operating temp, then you can use the max values in BS7671.
for an initial verification you should apply the rule of thumb (x 0.8) this is to allow for the increase of resistance as the circuit warms up.
 

Reply to Zs adjustment in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
625
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
955

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
345

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top