When measuring Zs values, does everyone apply the correction factors for temperature during fault conditions to the value?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Zs adjustment in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
The 80% values are in the osgthe 0.8 value is to be applied to the bs7671 values not the measured value
the 0.8 value is to be applied to the bs7671 values not the measured value
0.8 and 80% are the same thing surely? I meant i would measure zs of a circuit, take the maximum value and if its below the osg value then great there's room for manouver but of course the maximum values are in the bgb so as long as its below that its fineno u times the regs values by 0.8 and the ones in the OSG have already been corrected
0.8 and 80% are the same thing surely? I meant i would measure zs of a circuit, take the maximum value and if its below the osg value then great there's room for manouver but of course the maximum values are in the bgb so as long as its below that its fine
0.8 and 80% are the same thing surely? I meant i would measure zs of a circuit, take the maximum value and if its below the osg value then great there's room for manouver but of course the maximum values are in the bgb so as long as its below that its fine
Read what i've written! I've said its great if they're below the 80% but fine if they're below the bgb values!Those figures are for the Designer. The Inspector should ensure that the measured value does not exceed the corrected value.