B
buttonmoon
There is a general consensus that you measure Zs with sockets and calculate it with lights. The NIC lads say that the reason for the calculation is that otherwise you'd be forced to work live (electricity at work section 14). However as somebody on this site pointed out this doesn't actually test the MCB which is just assumed to have zero resistance. Could we not use the light fitting adaptor, obviously with only class 1 fixtures and measure directly thereby cutting out the laborious r1+r2 tests. We still need to verify the continuity and value of r2 with our wander lead for the forms but we would achieve a faster and more comprehensive Zs or is this still considered live working?