Hi This is my first post, I recently got 2382-10 and have started to study for my 2392. I understand there will be new qualification instead of 2392. Is this correct?
and comming to the point I changed a single socket and then used Megger 1710 to test phase to earth and phase to neutral loop.
My first problem: when I tried to find which MCB controls this socket I found it was not connected to any of the MCBs, If I turn off the main switch then it will turn off. So that means it was connected to main switch, I guess this is not allowed?
The wiring inside was one set of red-black -earth copper 6 mm2 and other set what looked like tin/aluminium wires of red-black-earth? This made me worry! it means a ring circuit and that means more sockets are connected to mains switch directly?
Any way after removing the old socket I put in new socket and started to measure
Phase to earth loop Megger 1710 showed the following: UL50V PFC 218A 1,06 Ohms
Phase to neutral loop Megger 1710 showed the following: UL50V PFC 1,25kA 0,18 Ohms
On page 49 table 41.3 gives info on type B breakers but which table do I use if it was connected to main switch?
I was already worrying about it and after these readings I need professional advice.
I take it this is dangerous situation and should change the connection from mains to a 32 A mcb.
am I right?
Your advice and analysis greatly appreciated.
Thank you
and comming to the point I changed a single socket and then used Megger 1710 to test phase to earth and phase to neutral loop.
My first problem: when I tried to find which MCB controls this socket I found it was not connected to any of the MCBs, If I turn off the main switch then it will turn off. So that means it was connected to main switch, I guess this is not allowed?
The wiring inside was one set of red-black -earth copper 6 mm2 and other set what looked like tin/aluminium wires of red-black-earth? This made me worry! it means a ring circuit and that means more sockets are connected to mains switch directly?
Any way after removing the old socket I put in new socket and started to measure
Phase to earth loop Megger 1710 showed the following: UL50V PFC 218A 1,06 Ohms
Phase to neutral loop Megger 1710 showed the following: UL50V PFC 1,25kA 0,18 Ohms
On page 49 table 41.3 gives info on type B breakers but which table do I use if it was connected to main switch?
I was already worrying about it and after these readings I need professional advice.
I take it this is dangerous situation and should change the connection from mains to a 32 A mcb.
am I right?
Your advice and analysis greatly appreciated.
Thank you