Hi

When filling in an Schedule Of Test Results, the top left box asks for ZS at DB.

On an installation with only one DB will the ZS at DB recorded as the same value as ZE.

After performing a ZE test can you reconnect the Earthing conductor and test for ZS and use that value.

Parallel paths will occur ?

Thanks
 
The PFC is usually highest at the origin of the circuit/supply. Hence Ze is used to calculate this. I would not be putting Zs at DB for the origin CU. I noticed that my iCertifi has also changed this from Ze to Zs which has puzzled me. Has something changed in regs? Am I missing something?
 
Last edited:
Ze is the external fault loop impedance of the supply characteristics carried out with the main earth disconnected.

Zs is the internal fault loop impedance and external fault loop impedance combined with the main earth connected, I don't see how you can transpose one with the other, they are two entirely independent measurements. Or am I missing something?
 
Did not think I would ever disagree with JW, but in his video above at 29:21 he states that the Zs at DB on the test sheet is for an additional board not the main board as detailed previously on a different page, yes you have repeated the information, but it allows the test sheet to stand on its own, the point is it's the main board test sheet not a supplementary board, IMO you append an additional test sheet with the full details of DB2 under "DB reference no" if needed.
 
Last edited:
It could be a case of differing interpretation.
I generally don't have the time or patience to watch such a video ....for three quarters of an hour. Looking at that particular certificate at the half hour point, as you say, It does look that way (he knows his stuff but he ain't half boring).
However, with NICEIC certs, there is the 'only if connected directly to the origin' factor, a good point, I feel.

[ElectriciansForums.net] ZS AT DB
 

Reply to ZS AT DB in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
726

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top