Not too sure what to read into this!!
New installl in my garage and doing initial testing
Socket Circuit ( radial )
R1 + R2 = 0.03 ohms using link method in CU
R1 + R2 = 0.03 ohms measured Line and CPC individually ( done this just to double check )
R1 + R2 = 0.07 ohms - of SWA from CU in house to CU in garage
Measured value of Ze = 0.26 ohms - in high current mode
Zs = 0.26 + 0.03 + 0.07 = 0.36 ohms
Measured value of Zs = 0.56 ohms - in no trip mode
A discrepency of 0.2 ohm ( more than the 15% tolerance of the meter) ( Fluke 1651B)
I tried taking Ze again using no trip mode to see what that gave but could not get a reading.
Any ideas anyone??!!