C
chiplard
Not too sure what to read into this!!
New installl in my garage and doing initial testing
Socket Circuit ( radial )
R1 + R2 = 0.03 ohms using link method in CU
R1 + R2 = 0.03 ohms measured Line and CPC individually ( done this just to double check )
R1 + R2 = 0.07 ohms - of SWA from CU in house to CU in garage
Measured value of Ze = 0.26 ohms - in high current mode
Zs = 0.26 + 0.03 + 0.07 = 0.36 ohms
Measured value of Zs = 0.56 ohms - in no trip mode
A discrepency of 0.2 ohm ( more than the 15% tolerance of the meter) ( Fluke 1651B)
I tried taking Ze again using no trip mode to see what that gave but could not get a reading.
Any ideas anyone??!!
Best to take "no trip" readings with a pinch of salt.they are ok for general tests but tend to give inaccurate results for actual circuit readings
Go with your Ze + (R1+R2) calculations,they are to be relied on much more than No trip Zs tests
I can't understand what you meant by
The test you made individually R1+R2 line and cpc individually :confused:
It was just a double check. The socket is right next to the CU so i tested the continuity of the individual cables. Just to verify the reading from the L-E link in the CU method.
Reply to Zs - Calculated and Measured Differences in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
6K