Hi All I'm new to this forum, and is my first question?
So he's the situation.
TNS supply - Ze measured - 0.41ohms
Main switch is RCCB , 100A 100mA
Main switch supplies a DB which feeds another DB ( this is the DB I am interested in) , the cable feeding this is a 2 core SWA, now I come to take a Zdb and the reading I receive is 4.7ohms. This DB is only 15-20 meters away so this instantly throws me out. Tested cable and cable is fine, resistance of the armouring is high but this is expected, not high to the point of there's a clear break in the SWA. Now out of interest I put in a tempory earth to essentially make a 3 core cable and have a dedicated earth. This reading gave back 0.50ohms as Zdb now this reading seems more acceptable.
Now lets go back to the main switch, it's a 100mA RCD so a touch potential of 50v can be applied to ohms law calculated. 50 divided by 0.1 is 500. So I would be allowed 500ohms at any point of the installation? Is this correct I have waffled abit so I might have missed something.
This is the first time i have come across this and I am just seeking answers thanks.