Setup:
Consumer unit fed via sub main from a 60A fused isolator switch. This is connected to the service head MET via a 2m earth connection.

How would one go about both calculating and documenting the Zs?
Would you be treating the fused isolator switch as it’s own db and therefore be documenting Zdb1 (at point of isolator switch) and Zdb2 (at consumer unit). Zdb2 would be be the reading minus Zdb1? Or would you do Zdb1 and then the R1 + R2 of the sub main?

I’m getting myself confused so if anyone would be kind enough to talk through how you’d test this setup it would be hugely appreciated?
 
So we have meter, 3m run to fused isolator, 15m run to CU
So it’s not a sub-main, it’s the consumers tails. In that case the 15m length of (hopefully) SWA is the distribution circuit in GBDamo’s post.

You can also measure the Ze at the CU the same way you would for a more traditional setup, but you need to remove everything other than the suppliers earth and the earth to the CU from the MET before you do.
 

Reply to Zs for a CU with sub main and fused isolator in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

For a TN system neutral is deemed at earth potential.
Replies
6
Views
379
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top