In other words anything on the ring will have (or should have) identical r1r2 readings whereas a spur will have the ring r1r2 reading plus the r1r2 for the legnth of cable on the spur.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Zs on a ring question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
In other words anything on the ring will have (or should have) identical r1r2 readings whereas a spur will have the ring r1r2 reading plus the r1r2 for the legnth of cable on the spur.
If the circuit is prorected by a 30ma rcd then the max allowed zs is 1667 ohms....so you are well under with 1.21.
edit....note that the 1667 ohms maximum zs applies to all circuits/mcb ratings where they are protected by a 30ma rcd....saves looking up the max zs readings for each protective device when filling in the schedule .
Ok, take on board what you say up to a point. Of course you would not expect a zs reading anywhere near the max value on a TN system. Problems with a high zs would normally become apparent before the zs is even tested...poor r1r2,or high ze,which would set alarm bell ringing. But If I do a PIR on an existing circuit,which probably has been spurred off and extended to the point where the measured Zs slightly exceeds the max value for the protective device,as long as other readings are acceptable and there is 30ma rcd protection it passes because the zs reading becomes irrelevent within reason.
This is a reasonable point
Regarding the points you made.
A 200ma rcd up front on all installations would not comply with the requirement for other circuits not being affected in the event of a fault on one circuit.
This happens with TT systems and doesn't seem to be an issue - as does one 80A cutout protecting the whole system
I dont see how R1R2,Zs,Ze and disconnection times become irrelevent....all need to be measured whether or not an Rcd is used to provide earth fault protection.
The readings become irrelevant when you have 250 to 1667 ohms to play with (depending on RCD rating), because as you stated, TN readings aren't gonna get anywhere near that. Also, to disconnect in 0.4 sec you could even have more play than that.
Whether or not an RCD is used for earth fault protection a reliable means of earthing has to be in place,the use of an RCD doesnt change that.
This is true - so all you have to do is confirm the earth path - readings wouldn't matter again.
Reply to Zs on a ring question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net