VoltzElectrical

-
Nearly Esteemed
Joined
Dec 31, 2010
Messages
2,216
Reaction score
1,052
What do we do about testing for ZS on a TT system? sorry, but never covered this in college. I know Ze should be below 200 ohms, and that the max Ze can be 1667 to give disconnection time when covered by 30mA RCD. But I've never given thought to actually testing and certifying a TT installation. What do you put on the form? Do you even test Zs at live points?

Sorry if this seems a bit basic, but college only covers TN system testing and I don't really deal with much TT.
 
test the same as for a TN system. the Zs readings will generally be a lot lower than expected, due to the gas and water bonding providing parallel paths and reducing the Ze.
 
yeah, say you get a Ze of 90 ohms, you may get a Zs of 3 ohms ( or anything, really ). you enter the value as measured, but for the max. allowed, it's 1667, as you mentioned.
 
ah, of course, the 1667 is the max value. Thanks again, and sorry for you having to explain the bleedin' obvious. I've been p to my eyes fault finding today and my head is fried!
 

Reply to ZS on a TT system in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
935

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
699

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top