At a property today I found that several lights have been taken as a spur of a ring main. At the end of the spur I get 1.33 Zs which is too high as it's on a 32A B MCB and should be lower than 1.16.
If I convert this to a fused 3A spur with FCU, can I used the 3A fuse to calculate the max Zs allowed? (which would be OK if so)