Zs on Minor Works | on ElectriciansForums
Discuss Zs on Minor Works in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
If you are adding something on a circuit, ie another light, fan etc, when doing the r1+r2 do you get that from the part of circuit you have added or from the last in line point on that circuit??
Thanks.
do you mean R1+R2? totally different to r1 and r2. R1+R2 is highes reading from all points on the circuit.
So if its not practical to add your circuit from the furthers point on the circuit, then you still dont need to test your circuit??
Thanks.
wherever you add, you still have to test. suppose you connected say a light half way along the radial circuit, and had snapped a cpc when tightening, you would then not get a reding further along the radial. so, last point on the radial should give the highest reading and prove continuity for the full length of the circuit.
Yes so basically test both but record he highest value which should obviously be the further est point. Just wasnt sure which i had to record.
Thanks.
yep, test at your fitting and at the furthest point. record the highest values. R1+R2 and Zs. compare Zs with max. allowed for the MCB/Fuse
Reply to Zs on Minor Works in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Unless the circuit is new or has recently been tested/certified by a.n.other, I'm not sure how you prove the circuit is 'safe' to connect to...
If this is a genuine change then throw it back at them, a nicely worded email explaining the additional testing requirements and paperwork charge...