hi all am i right in saying on tt systems the Zs reading will be a lot higher than the max? and is this exeptable?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Zs on tt in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
say the Zs on a ring main is 3.45ohms or higher on a TT are u saying 1667ohms is the max?
As Zs=Ze+R1+R2 then yes Zs on a TT system will generally be much higher than a TNCS system.
The maximum values are given for TNCS systems and therefore are not applicable to TT systems. The maximum value given in BS7671 is, I believe, 1667 ohms.
does this 1667ohms mean the max for all mcb sizes? o and what does IMO mean always wondered