hi all am i right in saying on tt systems the Zs reading will be a lot higher than the max? and is this exeptable?
 
hi all am i right in saying on tt systems the Zs reading will be a lot higher than the max? and is this exeptable?

It will depend on what system you have in place to enable disconnection times to be met (think RCD's).
 
Zs or Ze on a TT system the Ze should be less than 200ohms , the maximum Zs for correct operation is 1667 for 30ma RCD's and details found on table 41.5 page 50 of the regs , if you read reg 411.5 of the big red book
 
Last edited by a moderator:
whats the ZE has to be 200ohms at least I did one today turned out there is no rod at the end of the main earth conductors pikeys probably had it away,
Pict
 
Last edited:
The Zs on a TT will be higher than on a TN system but it can not exceed the max permitted.

Max permissible Zs on a 230V circuit with a 30mA RCD as additional protection is 1667 ohms.


Sent from my iPhone using Tapatalk.
 
As Zs=Ze+R1+R2 then yes Zs on a TT system will generally be much higher than a TNCS system.
The maximum values are given for TNCS systems and therefore are not applicable to TT systems. The maximum value given in BS7671 is, I believe, 1667 ohms.
 
say the Zs on a ring main is 3.45ohms or higher on a TT are u saying 1667ohms is the max?

Yes, for a 30mA RCD/RCBO protected circuit.

Are you working on such a system or are these study questions?
 
As the other guys have said you must have RCD protection for a TT system.
3.45 ohms Zs is very good for a TT system, what's the Ze?
Yes 1667 ohms is the max value for your certificate IMO.
 
As Zs=Ze+R1+R2 then yes Zs on a TT system will generally be much higher than a TNCS system.
The maximum values are given for TNCS systems and therefore are not applicable to TT systems. The maximum value given in BS7671 is, I believe, 1667 ohms.

The tabulated values in table 41.3 are for TN systems (TN-S AND TN-C-S)
 

Reply to Zs on tt in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
694
  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top