If people are having trouble understanding this magic '1667 ohms' number.. it is obtained from:

50V / 30mA = 50 / 0.03 = 1666.6666666666666666666666667, rounded up to 1667 ohms.
 
was about to say as widdler max. touch voltage 50 so 50/0.03mA = 1666 recuring rounded to 1667, but OSG says anything over 200 ohms should be considered unreliable due to soil drying out ect.
TT probs with B.Gas 'engineers' having plug in Go/noGo testers for supply to boilers having fail setting of a couple of ohms, trouble is they are always taught on TNS systems and don't understand TT.
 
was about to say as widdler max. touch voltage 50 so 50/0.03mA = 1666 recuring rounded to 1667, but OSG says anything over 200 ohms should be considered unreliable due to soil drying out ect.
TT probs with B.Gas 'engineers' having plug in Go/noGo testers for supply to boilers having fail setting of a couple of ohms, trouble is they are always taught on TNS systems and don't understand TT.

No, the On-Site Guide is referring to the RA value (the Ze if you like) NOT Zs values!
 

Reply to Zs on tt in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
829

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
694
  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top