If people are having trouble understanding this magic '1667 ohms' number.. it is obtained from:

50V / 30mA = 50 / 0.03 = 1666.6666666666666666666666667, rounded up to 1667 ohms.
 
was about to say as widdler max. touch voltage 50 so 50/0.03mA = 1666 recuring rounded to 1667, but OSG says anything over 200 ohms should be considered unreliable due to soil drying out ect.
TT probs with B.Gas 'engineers' having plug in Go/noGo testers for supply to boilers having fail setting of a couple of ohms, trouble is they are always taught on TNS systems and don't understand TT.
 
was about to say as widdler max. touch voltage 50 so 50/0.03mA = 1666 recuring rounded to 1667, but OSG says anything over 200 ohms should be considered unreliable due to soil drying out ect.
TT probs with B.Gas 'engineers' having plug in Go/noGo testers for supply to boilers having fail setting of a couple of ohms, trouble is they are always taught on TNS systems and don't understand TT.

No, the On-Site Guide is referring to the RA value (the Ze if you like) NOT Zs values!
 

Reply to Zs on tt in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
570
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
999
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
938

Similar threads

  • Question
Yes Table 3A that was in Appendix 3 of the 17th edition of BS7671 and in BS 7671:2018 (Blue Book) up to the release of BS7671:2018 +A2:2022 (Brown...
Replies
11
Views
952
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
792

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top