Correct, if you take your Ze + R1+R2 = say 1ohm , but your measured Zs= 2 ohm , then you should start looking for loose terminals etc.
but surely then, his R1+R2 readings would have been high if there was a poor connection.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Zs or (r1+r2) + Ze? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Correct, if you take your Ze + R1+R2 = say 1ohm , but your measured Zs= 2 ohm , then you should start looking for loose terminals etc.
but surely then, his R1+R2 readings would have been high if there was a poor connection.
A circuit I tested today for a solar p.v install which was fitted by another company last august, and the r1+r2 for the circuit was 1.08ohms, the cable was 2.5mm at about 8 metres in length. I was asked to record some lost data which included Ze and Zs. My metrel tester came back as a pass with ref to disconnection times (Ze was 0.16, 16a type B MCB) so according to BGB, 2.87ohms is the max Zs to meet disconnection times.
I did wonder why the reading was so high for such a short run of cable, but as it complied, and my job was just to record the data, I left it.
What would other people have done if they were doing a PIR or whatever they call it now? Would that have sent alarms bells ringing, or would you be happy with that?
Thanks Sam
Rest my case, that is what most do, which makes the testing worthless as the client is not going to know a good reading from a bad.And what are the chances the installation will be checked again ?I did wonder why the reading was so high for such a short run of cable, but as it complied, and my job was just to record the data, I left it.
Never stop asking questions Sam. Every day is a school day.
If you have done all your dead tests then you have measured R1+R2 then when it comes to live tests you measure your Ze, therefore there is nothing calculated about adding the two together as you have Measured both to obtain Zs
Reply to Zs or (r1+r2) + Ze? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net