Hey folk. i have been doing some testing and up to now i have had no problems. however today i have been getting a reading of >2000 ohms when doing a Zs test. i have been searching my brain and evrything else for a reason for this but cant find anything. this reading i am getting is right through the whole installation from the individual DB right back to the Main panel. would really appreciate it if anyone has any reason behind this. thanks.
 
What was the Ze/Zdb reading?.....if it's across the board it suggests a loss of main earth. Is the meter working correctly as well?
What is the purpose of this test....I hope it's not an EICR....if you cant work out a high Zs reading?
 
getting the same at the main panel. its powered by a generator and everything was fine yesterday so i am unsure as to how this has happened today.
its an installation for camp accommodation.
 
earth rods are intsalled around the gene. i am in afghanistan working and the ground isnt very good for getting a good Ze but i was still getting 0.15 ohms yesterday as a Ze reading so how this has changed overnight is beyond me
 
lol @ Mark. aye you're probably right. well it is somehow managed to rectify itself and i am now getting a Ze reading well within what it needs to be. think it might have been an issue with the meter but whoknows. thanks for your help guys.
 
earth rods are intsalled around the gene. i am in afghanistan working and the ground isnt very good for getting a good Ze but i was still getting 0.15 ohms yesterday as a Ze reading so how this has changed overnight is beyond me


I would have to beg to differ, if your getting Ra/Ze readings of 0.15 ohms!!!! ..lol!!!

I bet they're not using the short 3/8'' twigs for they're earth electrodes, more like the 10 foot 5/8'' or 3/4'' proper earth rods, and linking a good few of them out too...lol!!!
 

Reply to Zs Problem in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
698
  • Question
Just re-read the OP's post and it is an existing 5C SWA so presumably a 3P supply. For 40A and 150m you are seeing 6.6V drop or 1.65% of 400V 3P...
Replies
8
Views
882

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top