yeah. i'd make sure of the connections. as its affecting all circuits, any fault has to be at or close to the CU, then replace the RCD and see what effect that had on the Zs.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Zs reading help? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
i posted a similar scenario. Ze of 0.2 ish and a Zs of 350 every circuit. it was the crappy RCD.
the one i came across had Zs of 351 on all circuits. measuring on the outgoing side of the RCD gave a reading of 349.odd. but everything had been working fine for years. Ze was 0.2I dont get this,and have never experienced it myself.....Surely there is a direct CPC path to the MET,so there can be no excessive resistance there,and if you had a resistance of hundreds of ohms through the RCD contacts any loads connected to it would not work??
Perhaps the OP's shower was not faulty but it was the RCD's high resistance contacts preventing it from working properly??
I dont get this,and have never experienced it myself.....Surely there is a direct CPC path to the MET,so there can be no excessive resistance there,and if you had a resistance of hundreds of ohms through the RCD contacts any loads connected to it would not work??
Perhaps the OP's shower was not faulty but it was the RCD's high resistance contacts preventing it from working properly??
Putting the discrepancies on text readings aside for the moment, if you were replacing an appliance like-for-like then why are you testing and issuing a MWC? You have not altered the circuit, you are only replacing the appliance.
If more than 1 circuit is affected it sounds like a problem on the earthing conductor from method of earthing TNS to MET to earthing bar in CU where did you measure the Ze ? and did you do a continuity from the earth cable where you measured Ze to the earthing bar in CU where the CPC's are connected