Hi there,
In the process of testing a large property. TT system. Ra is 58.4 ohms so all good. But starting to test Zs and getting readings of 0.18 on sockets?
Why would this be?
 
i`ll bet its a redundant rod....

which of course would now be considered an extranious conductive part....and as such is bonded....

so the old earthing conductor to it has now become the earth rod`s bonding conductor...if you like...
 
I earned ÂŁ1000 a week the last two weeks Richard , and I may say thx to you for you patience over last few years on here, I'm getting good at this electrical stuff.....
Well done, I have just done my tax and I earned ÂŁ1000 (nearly) in the last year!
I must be a poor electrician!:aureola:

Thank you for your thanks and glad it has helped.

Just remember to keep getting better!
 
Or... To be precise (i bet), the water pipe is directly linked to next doors', who have... A TN system.

happens every now and again.

so (I bet) if you disconnected the bonds and re-ZS'd it'd be alot higher!

obviously the above is not recommended unless you have sole control of the installation etc etc
 

Reply to Zs readings on TT system in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
707
It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
786

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top