I've just finished an installation on a large outhouse around 50 meters from the main property, but I'm having issues with unusually high Zs readings within the new installation..
The nature of the installation is a TNCS system with 25mm tails & 16mm cpc Henley blocked from the main supply to a 60A sub-board with a 25mm2 SWA running 50 meters to the outhouses own 10 way RCBO consumer unit. (I was only able to ground the SWA at the supply end due to the SWA routing at the other end not alllowing me to gland into the consumer unit as it was laid in by the builder.)
My Ze reading at the sub-board came back around 0.19 and my Zs at the outhouse Consumer reading is 0.25 but when testing the circuits within the outhouse installation they all seem to come back unusually high for example 4 socket 16a radial - 3.89, 6 spotlights lighting circuit - 4.12 etc..
My R1R2 results come back absolutely fine so why are my Zs readings coming back so high and how can I possibly lower them?
I've been toying with the idea of installing a TT Rod at the outhouse to try and lower the readings but I'm not 100% sure if this would be sufficient.
Could anyone give me some advice?
The nature of the installation is a TNCS system with 25mm tails & 16mm cpc Henley blocked from the main supply to a 60A sub-board with a 25mm2 SWA running 50 meters to the outhouses own 10 way RCBO consumer unit. (I was only able to ground the SWA at the supply end due to the SWA routing at the other end not alllowing me to gland into the consumer unit as it was laid in by the builder.)
My Ze reading at the sub-board came back around 0.19 and my Zs at the outhouse Consumer reading is 0.25 but when testing the circuits within the outhouse installation they all seem to come back unusually high for example 4 socket 16a radial - 3.89, 6 spotlights lighting circuit - 4.12 etc..
My R1R2 results come back absolutely fine so why are my Zs readings coming back so high and how can I possibly lower them?
I've been toying with the idea of installing a TT Rod at the outhouse to try and lower the readings but I'm not 100% sure if this would be sufficient.
Could anyone give me some advice?
Last edited: